I didn't have time today to check the readings taken last week that have been discussed here as the client needed the RDC tripping issue sorted - which is is! Loose wiring in the switch plate.
I ran an Insulation Resistance test with 500V at the DB in the stable block. The system is TT and the stable has it's own earth electrode (according to the client, I haven't looked for it yet but will find tomorrow in the bushes somewhere...)
The IR test recorded the following:
LN 115 mOhm
LE 119 mOhm
NE 0.26 mOhm
There are 7 circuits on the DB (2 x ring final, 4 x lighting, 1 x another I forget what it is)
I will test each individual N to the earth block to see if it is just one circuit which is causing this reading.
Any kind thoughts would be welcome.
Many thanks.