Here are my measurements for 4 of the circuits so far. I removed each L, N and E and connected directly with crocodile clips (I removed the L's as one mcb had two circuits and it was just easy to remove the others as well although I know I didn't need to Andy):
All numbers are Mohms
Kitchen lights: LN 0.98 LE >999 NE> >999
Back Room Lights: LN 0.08 LE >520 NE> 460
Lighting Living Room Circuit 1 LN >999 LE >999 NE> 16.0
Lighting Living Room Circuit 2 LN >999 LE >999 NE> 0.05
Other pressures elsewhere today meant I wasn't able to continue the testing. There are 2 ring final circuits and the outdoor lights still to be tested.
Situation I'm in is that the client asked me to sort out a tripping RCD which I fixed, it was loose conductors in the light switch. She is happy for me to investigate the insulation resistance but doesn't want to pay for it of course. I have suggested that she should have a periodic survey completed as the building is very damp, has only been used occasionally and the wiring was done in 2002.
Can you guys help me to interpret these readings and let me know if you think I should press the client to agree to a periodic?
I am confident that no equipment was left on during the Kitchen/Back Room tests although the results might suggest there was? The building is a simple 3 room stable with just a fridge and an oil boiler for heating. I removed all the light bulbs etc... there are definitely no neons etc... I didn't remove the transformers for the lighting circuits in the living room and they have no earth connection at the transformer.
Looking at the LN readings for the Kitchen and Back Room is likely to cause overheating.
The 16Mohm would give a fault current of 560/230 = 0.035A - is this correct? (560 volts was the voltage I read as delivered during the test)
Many thanks.
All numbers are Mohms
Kitchen lights: LN 0.98 LE >999 NE> >999
Back Room Lights: LN 0.08 LE >520 NE> 460
Lighting Living Room Circuit 1 LN >999 LE >999 NE> 16.0
Lighting Living Room Circuit 2 LN >999 LE >999 NE> 0.05
Other pressures elsewhere today meant I wasn't able to continue the testing. There are 2 ring final circuits and the outdoor lights still to be tested.
Situation I'm in is that the client asked me to sort out a tripping RCD which I fixed, it was loose conductors in the light switch. She is happy for me to investigate the insulation resistance but doesn't want to pay for it of course. I have suggested that she should have a periodic survey completed as the building is very damp, has only been used occasionally and the wiring was done in 2002.
Can you guys help me to interpret these readings and let me know if you think I should press the client to agree to a periodic?
I am confident that no equipment was left on during the Kitchen/Back Room tests although the results might suggest there was? The building is a simple 3 room stable with just a fridge and an oil boiler for heating. I removed all the light bulbs etc... there are definitely no neons etc... I didn't remove the transformers for the lighting circuits in the living room and they have no earth connection at the transformer.
Looking at the LN readings for the Kitchen and Back Room is likely to cause overheating.
The 16Mohm would give a fault current of 560/230 = 0.035A - is this correct? (560 volts was the voltage I read as delivered during the test)
Many thanks.