543.2.7 Where the protective conductor is formed by metal conduit,trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a seperate protective conductor to an earthing terminal incorperated in the associated box or other accessory.
So this states that conduit is fine to use as a cpc
43.2.9
Except where the protective conductor is formed by a metal covering or enclosure containing all of the conductors of the ring, the circuit protective conductor of every ring final circuit shall als be run in the form of a ring having both ends connected to the earthing terminal at the origin of the circuit.
I would read that as conduit is fine as the cpc for a ring final, so long as continuity/R2 checks out.