Well maybe they want you to design the circuit fully.. and not just calculate the voltage drop..
they don't try to confuse you searley...the question i put on was of a collage paper.it does not say what cable to use.collage lecturers. why don't they just make it easy then try`ing to confuse. a--- holes
making a few reasonable assumptions from the details given I would be guessing on a domestic T&E run!!a 3kw load is supplied from a 230v, 50hz supply.
e.g. MAYBE SINGLE PHASE ?
the circuit is protected using bs 3036 (rewirable) fuse and is situated 15m away from the db .
e.g. MAYBE TYPICAL DOMESTIC USE FUSE & DISTANCE?
it is run with one other circuit and is buried within the buliding material of the intallation.
e.g. MAYBE T&E IN PLASTER WITH A SOCKET CIRCUIT?
the temp within the installation can be assumed to be 25c.determine the volt drop ?
e.g. NOT A HOT FACTORY ENVIRONMENT REQUIRING HEAT RESISTANT CABLE SUCH AS PYRO?
The volt drops in the On Site Guide pages 133 & 134dont think VD tables are in OSG. you need the regs for that. there are a few pages with VD for various cables
In the words of that dog on the car insurance ads..BS7671 pages 274-317 cover cable VD (did I get this before Special Applaud Smiley)
Well done oh wise and wonderful vet'ish type man!!!Blushing:x:xI get you upto the point you magically decide it's 6mm T&E. Why not 2.5mm 4mm etc?