:^O :^O Just put me eyes back in!
I didn't notice some of your previous answers m8!
So we are all PVC T&E out of CU... at least thats a good point:^O
Q3c) Is the voltage present with all switches OFF and bulbs out? 50 bulbs to be removed
Q3d) When you get the voltage are ALL of the lighting circuits switched OFF at CU? All switched OFF and voltage on CPC. Tried to remove each circuit, one at a time, voltage still present, reconnect one a time voltage reappears.
KItchen lights, living room are all low voltage rate lights cpc's are not connected. The connection with power, switches and lights are all bodged together on connector blocks.
This could be a couple of faults! together..
some cpc touching something it shouldn't & circuits not independent of each other!
Re (Q3d) if you are only removing power one circuit at a time...
and you have bulbs left in, and switches in the on position,
and you have neutrals joined together somewhere between circuits...
one of the other live circuits can put a voltage back onto the one you assume is disconnected ! :|
this is the simple principle
I suspect your 80v is coming somewhere between joined circuits though bulbs or transformer acting as a potential divider between your three floors
1/3 of 240v = 80v just a hunch!
In a nutshell!
you need to diss all of the lighting circuits off at the same time do all proper dead tests to identify any anomalies with any or all of the circuits!
then rebuild back up from there!
P.S. I dont envy you!