What fault can turn a TT into a TNCS and disable the RCD?

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

sparkytim

Well-known member
Joined
Mar 14, 2010
Messages
1,809
Reaction score
1
So here is another interesting Fault situation.

Testing Zs on a TT system socket and gets 1.2 ohms.

Ra known to be 64 ohms

On testing RCD it fails to trip at 1x, 5x and even with a 25 Amp Loop test, but operates on Test button.

What was the fault causing this and why?

 
do you want the answer, or is this aimed at the students?
Aimed at students steptoe so do not answer

---------- Post Auto-Merged at 20:52 ---------- Previous post was made at 20:52 ----------

:yawn :innocent:put the kettle on

 
Thanks for holding back Steps, just as an aside this is one Dangerous condition that CAN occur with TT. ;)

 
tim, I hadnt looked at the forum,

so I didnt know if it was a fault or a fault scenario.

my bad. :|

it can, but under those conditions then there is another massive change that takes place to negate the effect the fault has in situations of direct/indirect contact.

 
It could be some time before you get a decent reply, hang on for the inrush of students, they will all be out on the town tonight.

 
Reminds me, once I segregated a Garage from a TNCS, banged a stake in and got a 1 ohm Ra.

Only sliced the outer sheath on the Swa and picked up the Armour CPC again! :innocent

That is NOT the answer to this one by the way

 
Last edited by a moderator:
and who exactly buried the SWA?and what about the bit where you check for underground services before digging?

or banging rods in!!!! :D
Pre existing SWA, didn't have me CAT handy.

 
I must be the only student who ain't out getting drunk from the lack of replies by students lol:)
your just old and worn like the rest of us, this is our pub, we sit in here and get drunk. :D

---------- Post Auto-Merged at 21:50 ---------- Previous post was made at 21:48 ----------

Pre existing SWA, didn't have me CAT handy.
another 1" and you wouldnt have need it,

bad day explode

:slap

 
Guinness

:Salute

---------- Post Auto-Merged at 21:53 ---------- Previous post was made at 21:52 ----------

I think Apache told him to hammer the earth rod in using a cat and it would save any problems. ;)

 
My ears are still ringing:slap

Disclamer NO PETS were harmed in this activity

 
Last edited by a moderator:
Ok I'll have a bash...

TT to TNCS needs connection between cpc and N.

As RCD is balanced ,then a cross wire to keep both conductors balanced would disable it....my answer either short or crossed wiring on RCD circuit ?

 