Been to view a new install (first fix on Tuesday), supply put in this morning.
Nice new ampey meter & service cutout (nice blokes never sealed the uot terminal on the meter ) & in pencil scrawled on the wall EFLI 0.29.....no pme label on backboard....nothing on the paperwork left with the customer to say pme.
So would you just go along with the efli being low enough & assume pme or TT the install.
Me I was gonna TT it if I got no joy from SSe.
.
.
.
.
.
.
Well I called SSE & was given the number of the lads that put the supply in & was told by the girl on the help desk & the lads who did the install, when I managed to get hold of them;
"It's now common practice for sparks to measure the efli & if it's below 0.35 connect the customers installation as pme (tnc-s)"
"I left it written on the wall for you & we dont put the lables up now on new supplies as they are all pme."
Nice new ampey meter & service cutout (nice blokes never sealed the uot terminal on the meter ) & in pencil scrawled on the wall EFLI 0.29.....no pme label on backboard....nothing on the paperwork left with the customer to say pme.
So would you just go along with the efli being low enough & assume pme or TT the install.
Me I was gonna TT it if I got no joy from SSe.
.
.
.
.
.
.
Well I called SSE & was given the number of the lads that put the supply in & was told by the girl on the help desk & the lads who did the install, when I managed to get hold of them;
"It's now common practice for sparks to measure the efli & if it's below 0.35 connect the customers installation as pme (tnc-s)"
"I left it written on the wall for you & we dont put the lables up now on new supplies as they are all pme."