The bottom line is if your quote for an all RCBO board (not that the customer cares, but one can frighten them) is accepted all well and good but you have to consider that leakage currents are a parasitic load that makes the meter tick over. The problem with the regs is that they expect you to do an earth leakage test on all circuits and Zs to determine the required design. Instead, the tests are conducted if at all post installation.
The real problem that has not been addressed by the regulator is that manufacturers' of consumer products are not obliged to provide an RCD Declaration as is required by GTI makers. How is an electrician expected to know that a Type F RCD/RCBO is required rather than a Type A or Type B? Its all down to the experience of the electrician and a lot of guess work.
Have you actually read 531.3.2 (ii) in the CURRENT regulations? or are you still working to amendment 1, or earlier?
Also current regs 531.3.3 (starting on page 156), gives a reasonable description of the different types of RCD...
and some guidance regarding their usage.
I am a trying to find the regulation that you think requires an earth leakage test on all circuits?
and/or which are the model forms where you document this earth leakage current?
This thread has a significant amount of incorrect / outdated information... (mostley from a single contributor).
which in my opinion suggests poor practice and incorrect materials being recommended in order to gain business from an uneducated customer!!!
Which is a significant conflict with the guidance of 134.1.1 (Good workmanship, Skilled or instructed persons & Proper materials).
Dual RCD / Split-Load / High integrity CU's are about as up-to-date as writing a cheque when you pay for your weekly food shopping at Tesco!!
I am trying to remember when I last fitted a dual RCD CU -Vs- writing a cheque?
OR when a customer last paid me by cheque??
Bank transfer, or Card payment, or Google/Apple pay etc. are the norm,
or occasionally cash on jobs less than £75!
What used to be sold as "dual RCD"/"high integrity" Cu's, are so Old-Hat.....
I didn't think anyone other than "DIY", "Bob-The-Builder", "Kevin-The-Kitchen-Fitter", "Barry-The-Bathroom-Fitter", OR "Larry-Loft-Converter", actually bought or fitted them?
If you have any half decent suppliers, the cost difference for full RCBO -vs- 'not very high integrity' is so small it is a no-brainer, to install a better value solution for your customers.
[ But even though I have been doing this job, working for myself for well over 20+ years. Passed all relevant C&G exams, as & when BS761 has been updated/amended. It is possible I may have missed "the bleedin obvious"....
So if you can please tell me the regs that suggest Dual RCD are a good solution..
And how & where you document these earth leakage values you mention?????
Or is it all 'Smoke & Mirrors' plus 'Tosh & Waffle', trying to back-up a very poor design solution using a single or dual RCD to protect multiple circuits!?
I cannot believe anyone who has had to do fault finding on a split load board with no-RCBO final circuits, would ever consider a non-full-RCBO CU to be an economical solution!