Been to look at it today and its a mess.
There has been 2 sparks there before me, 3 plumbers, has been well and truly tinkereed with.
Now info I know
Feed for system in kitchen beside programmer and boiler
1. danfoss fp715 programmer in kitchen
2. Potterton boiler lpg 50e L-N-E-SwL in kitchen
3. hot water tank with sunvic sz6355 actuator in loft
4. cylinder stat on tank in loft.
5. 2 x pumps in loft
6. heat exchange in loft.
7. 2 x anti boil stats fitted to exchange.
8. one hell of a messy control terminal box in loft.
Now the antiboil control system works like this. In the event of an overheat situation anti boil stat number 2 which in this case is on the LHS of the exchange is set at 85 degrees C will MAKE and and switch on the space heating pump.
If the space heating pump or electricity should fail, antiboil stat 1 on RHS of the exchange set at ?? (cant read the temp on paperwork, but stat was on 45 degrees C )will break and allow spring open motorised valve to open. this will switch off the gas fired boiler and open the cylinder circuit.
Now based on thi information I have drawn up a wiring diagram and would Like all you cahps to have a look at it and tell me if it will work and if not pointers as to where my mistakes are.....
Yours under pressure
Macca