Nigel sparks
Member
- Joined
- Nov 23, 2018
- Messages
- 16
- Reaction score
- 0
I think it must be a designer idea but he or she should of refused as pipe is not earthed , way to small, bend radius too tight and no cable protection on entry or exit of pipe
 we normally do this to suite singles though. Personally I think I would have taken the pipe into the PVC box to allow a discreet earth bondDo you think it would comply then? It’s installed in a restaurant toilet that I went to last night. You would never install  metal conduit that wasn’t earthed.
Enter your email address to join: