Would you or wouldnt you?
M107
Billy-the-Kid
Feb 18, 2008
5,562
28
Berkshire
Mate of mine is using the following on his NICEIC DI assessment.
Instead of running a sub from the house cu at the front of the mid-terraced (I advised up the front of house into loft & drop down the back of house) he (because of cost its a mates rates job) has extended the house only ring final circuit down the garden 10mtrs to garage terminating into a cu via insulated adaptable box.
New cu set up as TT with 30mA rcd mainswitch & new lighting circuit 6amp + 3x sockets 16amp.
I said I wouldnt be happy to use it as an assessment peice myself.
SPECIAL LOCATION
Trailer Boy - Electrician.
Mar 28, 2008
13,633
317
Mate of mine is using the following on his NICEIC DI assessment.Instead of running a sub from the house cu at the front of the mid-terraced (I advised up the front of house into loft & drop down the back of house) he (because of cost its a mates rates job) has extended the house only ring final circuit down the garden 10mtrs to garage terminating into a cu via insulated adaptable box.
I assume he has put double pole isolating switch of some sort where the circuit leaves the house?
Cuz if there was a fault on the supply to the garage, tripping the ring circuit
you would want some easy way to isolate the external wiring to get all your sockets back on..
As for NICEIC assessment.
If they want to prove the circuit readings,
it could be a bit of a swine unplugging everything off the ring to do Ins Res readings..
I assume they would treat this a one complete circuit ..
'MCB - Ring - Sub - External building'..
unless they just look at it as from the Sub onward?
I guess they would want to prove the whole circuit ring and all..
because the extra load will be on the ring! ?:| ? :|
Be interesting to see how they approach it? ?:|
I have always used either easy radial, cooker / shower circuit
whole CU
whole re-wire.
The NIC man has always asked for a straight forward circuit to verify readings & testing procedures etc.. ???
As you say.. I wouldn't pick this job either as a assessment piece! :(
Feb 14, 2008
7,471
21
Cloud Cuckoo Land
Has the house ring been extended or a spur off this ?
The Niceic published a paper recently about overloading a ring on one leg, although this probably would not happen in this scenario 22A could be drawn at the garage C/U.
They were particularly concerned about grid switches in kitchens supplying the whole room from one point whilst the ring continued with hardly any load for quite a few more meters, thus putting a strain on the shortest leg. Not a lot of sparkies think of that.
SPECIAL LOCATION
Mar 28, 2008
13,633
317
Has the house ring been extended or a spur off this ?The Niceic published a paper recently about overloading a ring on one leg, although this probably would not happen in this scenario 22A could be drawn at the garage C/U.
Those are my sort of concerns as well, Mr Slipshod... :)
I just feel these sort of scenarios best kept away from inspection assessment in case Mr inspector decides to asks questions...
that you haven't already verified yourself!!! :eek: :O
Better to offer a final radial direct back to CU suppling garage..
far easier to justify all your calcs & selection & erection! :D
M107
Billy-the-Kid
Feb 18, 2008
5,562
28
Berkshire
From what I gather he has litteraly extended the ring ( as in two legs) to the insulated adaptable box, where the cpc has been terminated, then taken line & neutral into cu main switch/rcd & installed as TT.
I just think he's asking for a bucket load of hassel on the assessment.....mine last week I got picked up for not enough clips on a sso radial done in MICC :_|
still got the thumbs up though ( although he did say it was unusual to see a garage wired in MI :^O (it was spare so thought I'd use it :p )
SPECIAL LOCATION
Mar 28, 2008
13,633
317
From what I gather he has litteraly extended the ring ( as in two legs) to the insulated adaptable box, where the cpc has been terminated, then taken line & neutral into cu main switch/rcd & installed as TT.I just think he's asking for a bucket load of hassel on the assessment.....mine last week I got picked up for not enough clips on a sso radial done in MICC :_|
I would concur there M107!
be interesting to hear how he gets on??
Prove us all wrong.. :(
egg on our faces! :(
go eat our hats etc.. :_|
OR not???????????? ?:| ? :| ?:| ? :|
M107
Billy-the-Kid
Feb 18, 2008
5,562
28
Berkshire
I would concur there M107!be interesting to hear how he gets on??
I'll let you know, he's due for assessment mid May.