Hi all
Looked at a basic wiring set-up with programmer (dual channel), mid position valve, cylinder stat (no room stat) and Keston boiler. Heating engineer stumped so I had a look. If CH is selected at programmer the boiler fires as it should; when CH is set to off - the boiler remains on? Measured 89V at switched live. I know Honeywell valves 'leak' a bit of voltage - not normally enough for this to happen. Heating engineer had replaced the valve twice. What's occurring?
Looked at a basic wiring set-up with programmer (dual channel), mid position valve, cylinder stat (no room stat) and Keston boiler. Heating engineer stumped so I had a look. If CH is selected at programmer the boiler fires as it should; when CH is set to off - the boiler remains on? Measured 89V at switched live. I know Honeywell valves 'leak' a bit of voltage - not normally enough for this to happen. Heating engineer had replaced the valve twice. What's occurring?