I would welcome any views and assistance on an installation in an hospital that I found today
I was asked to wire and fit sockets for a ring main to some dado trunking that had been erected by a builder
This was being wired from a single phase dist board which had a faulty 100m/amp rcd main switch
A couple of lights were added to an existing circuit
After wiring, tests were made and the Zdb was 4.54 ohms
This test was then taken at the main dist board with all earths still connected and simillar reading was obtained
Nobody with maintenance responsibility was at this small hospital,however I managed to talk to an estates manager that they contacted for me
I asked for access to where the incomer was located, but no help off anyone,
this was to look at what system earth was present
I would expect that it may be Tns,but am guessing
The estate manager was very indifferent to any problem,they have a maintenance crew and he would send their electricians to have a look as he put it,( because they are going to close it in a year and didn't want any money spent) and could I make the sockets live
If I were to fit rcbos instead of the 3871/1 mcbs in the board,does this comply with regs (given in a TT system the max Zs for a 30m/amp rcd is 1667 ohms) although the system is probably Tns and the Ze appears to be well above stated values for operation of these mcbs for a Tns
It was my intention originally to omit Rcd protection using the skilled instructed person bit.this changed my thinking
As a sort of postscript
When I replaced the main dist board cover after talking to this person,I looked at the Mcbs and noticed one tripple pole was off,I thought I had inadvertantly knocked this off and reset it,there was one almighty bang as I did so,I left it off ( this was nothing to do with the new install,but it makes me very concerned as to the state of this installation if a faulty circuit like that has been left connected
Your views would be welcome,thank you
I was asked to wire and fit sockets for a ring main to some dado trunking that had been erected by a builder
This was being wired from a single phase dist board which had a faulty 100m/amp rcd main switch
A couple of lights were added to an existing circuit
After wiring, tests were made and the Zdb was 4.54 ohms
This test was then taken at the main dist board with all earths still connected and simillar reading was obtained
Nobody with maintenance responsibility was at this small hospital,however I managed to talk to an estates manager that they contacted for me
I asked for access to where the incomer was located, but no help off anyone,
this was to look at what system earth was present
I would expect that it may be Tns,but am guessing
The estate manager was very indifferent to any problem,they have a maintenance crew and he would send their electricians to have a look as he put it,( because they are going to close it in a year and didn't want any money spent) and could I make the sockets live
If I were to fit rcbos instead of the 3871/1 mcbs in the board,does this comply with regs (given in a TT system the max Zs for a 30m/amp rcd is 1667 ohms) although the system is probably Tns and the Ze appears to be well above stated values for operation of these mcbs for a Tns
It was my intention originally to omit Rcd protection using the skilled instructed person bit.this changed my thinking
As a sort of postscript
When I replaced the main dist board cover after talking to this person,I looked at the Mcbs and noticed one tripple pole was off,I thought I had inadvertantly knocked this off and reset it,there was one almighty bang as I did so,I left it off ( this was nothing to do with the new install,but it makes me very concerned as to the state of this installation if a faulty circuit like that has been left connected
Your views would be welcome,thank you