Ok guys & Hi not been on for a while trying to learn new stuff and skills and bring back old ones forgotten, Lol
Question, Ze & Zs testing domestic.
ze Consumer unit main switch off, main earth removed from met, proceed with test, Ze yes, on loop setting
Zs at sole Db consumer unit, main switch on, all rcds breakers etc off. Fluke 1654B 3 lead test Phase, Neutral, Earth. placed at main switch energised terminals and earth bar, is this good enough for Ze as a spark said I needed a designated efli tester. Though fluke 1654B on hi current is good enough as it tells me both KA value and impedance
Any light on this would be great please guys trying to progress in testing area. but confused from other sparks remarks on sites.
Ta
Question, Ze & Zs testing domestic.
ze Consumer unit main switch off, main earth removed from met, proceed with test, Ze yes, on loop setting
Zs at sole Db consumer unit, main switch on, all rcds breakers etc off. Fluke 1654B 3 lead test Phase, Neutral, Earth. placed at main switch energised terminals and earth bar, is this good enough for Ze as a spark said I needed a designated efli tester. Though fluke 1654B on hi current is good enough as it tells me both KA value and impedance
Any light on this would be great please guys trying to progress in testing area. but confused from other sparks remarks on sites.
Ta