Photos and a sketch of the circuit would clarify matters a lot
Pretty clear to me he has put a 32A switch into the ring final by way of a 4.0 radial.
He explained:Pretty clear to me he has put a 32A switch into the ring final by way of a 4.0 radial.
He does not say how he connected the radial into the final ring.
Hi Tim.Thanks for all your comments although none seem very helpfull, all equipment is individually swtiched off with the exception of 1 small negative ion generator and 3 small dc transformers no more than 0.5amp each. If it was in rush current (which it isnt) the mcb would trip when I switched it back on, which it doesnt. The circuit itself is fault free Ive checked it ( I have 2391). I think perhaps the best answer is to change the MCB and the 32smp switch, which does seem a bit clunky. Changing for a motor rated breaker seems a bit pointless as there is virtually no start up load.
Dare I asked what testing you have done ?
Photos and a sketch of the circuit would clarify matters a lot
Pretty clear to me he has put a 32A switch into the ring final by way of a 4.0 radial.
That’s what I suspect but the OP isn’t really coming forward with clarity