Completing test sheets on circuits. With rcd protection and and rcd socket outlet

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Nige mart 50

New member
Joined
Sep 19, 2024
Messages
1
Reaction score
0
Location
Manchester
You have a DB with 100mA protection

You have a circuit with a 32a socket outlet with a 30mA rcd fitted - protecting the socket outlet

When completing the test sheet I’m on the understanding , the rcd protecting that circuit is 100mA and that information will be inputted on the test sheet

The socket outlet itself 30mA will be tested and recorded say on a ppm sheet or recorded on notes of the test sheet , as it is not protecting the actual circuit

A few lads at work seem confused by this and are saying you should write 30mA on the test sheet for that circuit test the socket and record them results on the test sheet

which I disagree with that

Also what if you had a circuit with multiple rcd socket outlets ?
They say test them and record highest

Same again I’m on the understanding the rcd in the DB protects that circuit
And the socket outlets should be tested separately and recorded on a Ppm sheet or something similar
 
I agree with you, you should record the protective device and additional protection provided for the entire final circuit.
Otherwise you create the impression that the circuit has additional protection that doesn't exist.
 
I agree with you, you should record the protective device and additional protection provided for the entire final circuit.
Otherwise you create the impression that the circuit has additional protection that doesn't exist.
The 100ma would not be additional protection.
 