13A spur - how many
jack2017
May 8, 2017
12
West Midlands
Related to my pond pump thread but I thought this may be simpler - hope thats ok
I have a single 13A socket with a spur taken off it.
Ideally I would like to add a second spur to feed my pond pump.
question is - what is my allowed method of doing this as I'm looking for
the simplest implementation?
Looking at the 433.1 reference jpg posted in another thread I'm not sure but can I
1. Blank off the socket and feed 2 spurs from 16 or 30A chocolate block from inside
the box. (the feed would not be fused in the socket box then although it is on RCD)
2.  Install a double switched socket and take the second spur off the second socket
3. is there something else I could or must do
I just want to get this done as quickly and simply  as possible.
If you didnt read my pond thread the spur I'm feeding to is 1.5mm SWA cable to
a pond pump.
thanks
jack
You have a single 13A socket with a spur from it.
Add a new 13A single socket next to that one, wired as part of the ring, and take your new spur from that.
Assuming the socket in question is indeed part of a ring final, if not you have bigger problems.
An option might be that if the single socket is part of the ring swop it out for a Fused Spur then coming of the load side you can have multiple sockets limited by load that will be plugged into them, there was a picture in the original 17th appendix 15 showing this.
This one I think.
Yes sidewinder - thats the jpg I had to look at.
ProDave makes a good point - how can I confirm the socket I'm looking at
is fed off the ring and is not a spur itself? All the wiring in it
seems to be 2.5mm solid core if that helps.
The second option top left on the diagram looks like I can just
wire my external box right in?
You check it's part of a ring, by disconnecting the two cables in the back of a socket, and doing a continuity check on all 3 cores to ensure they are indeed joined together somewhere, and the resistance reading you get is plausible for the expected length of the ring.
The same way you will confirm that any alterations you do are connected correctly. e.g. you will need a low resistance ohm meter to verify the continuity up your CPC is appropriate for the length of cable fitted. The same meter can be used to measure the L->L, N->N, E->E   loops at the socket you intend to spur off.  The L&N values should be within a gnats whisker of each other and both expected values based on the probably length of the ring. The E->E (CPC) will be proportional to the L&N dependant upon the size of conductor used in your wiring. (1.5mm or 1.0mm):2.5mm. If the whole continuity of the ring is not verified to the values you would expect I would think you need a bit more investigations before extending anything.