Hi all just been to my cousins house to help with his new kitchen, some extra sockets ect.
First find was 32amp breaker for kitchen ring which was not a ring but a radial with 5 sockets on it and a spur form a spur also ( so a good start to the night ).
Sorted the sockets then looked at his new cooker its a large range with gas hob 2 ovens and a grill measuring 14.5KW.
Had a look at regs and came up with 29amps for load ( first 10amps then 30 percent of full load ) but i feel this too be a little low and was thinking on changing his existing 6mm cable to a 10mm. The 6 mm is ok for the original calculation but would like to hear from the forum on this thanks again. O)
First find was 32amp breaker for kitchen ring which was not a ring but a radial with 5 sockets on it and a spur form a spur also ( so a good start to the night ).
Sorted the sockets then looked at his new cooker its a large range with gas hob 2 ovens and a grill measuring 14.5KW.
Had a look at regs and came up with 29amps for load ( first 10amps then 30 percent of full load ) but i feel this too be a little low and was thinking on changing his existing 6mm cable to a 10mm. The 6 mm is ok for the original calculation but would like to hear from the forum on this thanks again. O)