Just rewired a ring of about 50m,,,no difficult runs
tested it and N-CPC 280 meg
others around 800 meg
disconnect the ring and check each length between sockets and get
1000 meg +
connector block each socket outlet same readings on full ring
connected together its pants.
tested a reel of same cable 70m approx and the readings are around the
300 meg mark
test 80m of 1.5mm (same manufacturer )still on the reel and get 900+ meg readings
the cable is clipped only and has not been plastered yet
have i got a bad batch of 2.5mm ?
Cheers
tested it and N-CPC 280 meg
others around 800 meg
disconnect the ring and check each length between sockets and get
1000 meg +
connector block each socket outlet same readings on full ring
connected together its pants.
tested a reel of same cable 70m approx and the readings are around the
300 meg mark
test 80m of 1.5mm (same manufacturer )still on the reel and get 900+ meg readings
the cable is clipped only and has not been plastered yet
have i got a bad batch of 2.5mm ?
Cheers