so look at the control gear and see if its wired star or delta...
or just go buy a new one, less hassle
or just go buy a new one, less hassle
Deke,
I don't think resistance will tell us, each of the windings are equal resistance.
Letting the ends be as you have labelled them a, b, & c.
a to b will be two windings, b to c will be two windings, c to a will be two windings, if star.
a to b will be one winding, b to c will be one winding, and c to a will be one winding, if delta.
Trouble is we don't know what the resistance of one winding is, so we also don't know what the resistance of two windings is either.
Not blindingly obvious really.
Hence why I posted.
I'll have a look at what technician has posted later if I get time.
I think we need to stick known currents & voltages in and see what we get as an initial guess.
Sidewinder; I will have to post the sketches and yes,I have a theory, and I'm going to go through what technician has posted next.
Deke,...
Bad decision ....heating guys run it up and a winding failed . I never found out why 7 pumps were Star and that one was Delta.
I "think" it "has" to be a black box approach Technician, as we don't know if it is Y or D, and there is no way to tell, apart from the meter readings...I think I have the answer.....using a "black box" approach.
Just examining my reasoning.
You told the store man that he was delinquent in keeping records, and now you also have a black eye to go with the motor that you can't identify the winding configuration of!curses upon theses storemen who cannot maintain the records system....look at the trouble they have caused
:slapI "think" it "has" to be a black box approach Technician, as we don't know if it is Y or D, and there is no way to tell, apart from the meter readings...
You told the store man that he was delinquent in keeping records, and now you also have a black eye to go with the other one your wife gave you
I have split the post into 3 sections, and tried to sketch out the options, my comments are on the sketch, I don't see how this can work, you are suggesting connecting an ammeter in parallel with one of the windings, thus it will merely act as a shunt.I have had an idea.
Arrange to pass a small direct current through
the motor windings using a small power source,
like a battery.
Measure said current. Do this three ways.
Record results. They should be the same.
Now, let one terminal be A the next B and the next C.
The battery and its ammeter are connected to A & B.
Measure the voltage between terminal A and C and
then B & C.
----------------------------------------------------------------------
If this measured voltage is half the applied voltage,
i.e. V (A/C) and V (B/C) is half voltage A/B then
chances are this is a delta connected machine.
-----------------------------------------------------------------
Now, connect another ammeter so that it is teminated
at winding C at one side and to A on the other.
This puts the windings at A and C in parallel. This
ammeter should show half the reading of the other one
which is measuring total current.
If you do this on a delta connected motor you will short
the energy source and this ammeter will go off scale.
Hope this is clear but I am open to suggestions & questions.
I have sketched this out on a cigar box and it looks OK.