Yes Plumber, I thought you said you were going to change that signature?
LOL- so i did, any suggestions? be niceYes Plumber, I thought you said you were going to change that signature?
But im not suggesting there's no alternative, Just stating an RCD may be used for ADS.Gentlemen I can understand why sidewinder is reluctant to post why any installation can be designed and engineered without the requirement for RCD,s even TT can be engineered so that a RCD is not required.
Is this sentence not a contradiction in itself? - or have I read it wrong?Am I missing the point here? ......in the event of a Line to neutral fault, which a fuse or MCB will interupt very quickly assuming R1+R2 values are met for the appropriate device.
...
411.1 Automatic Disconnection of supply is a protective measure in which:
i) basic protection is provided by basic insulation of live parts or my barriers or enclosures, in accordance with section 416, and
ii) fault protection is provided by protective earthing protective equipotential bonding and automatic disconnection in case of fault, in accordance with reg 411.3 to 411.6
Where this protective measure is applied, Class 2 equipment may also be used.
Where specified the requirements for additional protection shall be provided by an RCD having the characteristics specified in regulation 415.1.1
Basically there is no 1 thing that acheives ADS!! ADS is as it says on the tin, automatic disconnection of supply.411.4.4The following types of protective device may be used for fault protection:
i) An overcurrent protective device
ii) An RCD
note: Where and RCD is used for earth fault protection the circuit should also incorporate an overcurrent protective device in accordance with chapter 43
Sidewinder,you have just thanked sellers for his post which is the same as my post to which you said was no help? :|ADSi (Basic protection by) - Insulation of live parts, or barriers or enclosures.
ii (Fault protection by) - (1)Protective earthing, (2)protective equipotential bonding, (3)automatic disconnection.
(3) Automatic disconnection may be achieved by a Fuse, Circuit Breaker or RCD.
Two areas people seem to get confused with, (1) A RCD may be used for automatic disconnection, and (2) protective equipotential bonding is part of ADS.
Hope that helps