Hi Guys, I installed a new 17th eddition CU over 3 weeks ago tested and working fine. I got a call from the lady of the house tonight to say her sockets keep going off....then she went on to say she has just had some new flooring laid in the kitchen and when she turns her electric cooker on, all the sockets go off and she thinks the men must have mooved the cooker while laying the new flooring.
Other than me inspecting for a loose conection or kinked/stretched cable from the cooker to outlet has anyone any suggstions before I go there to try and find the fault.
Chas
maccarooni
Jul 13, 2008
340
hi pb. Is it just the sockets going off or the rcd tripping ?
Macca
Guiness DrinkGuiness DrinkGuiness Drink
Power Ball
Jul 10, 2008
171
Yorkshire
Hi, Just think it's a bit odd that all was working OK for over 3 weeks then the minute she has new flooring in the kitchen this happens after the cooker has been pulled out and put back..?
Cheers
Guiness Drink
maccarooni
Jul 13, 2008
340
It is possible that they have damaged the cooker cable. Giving you a small neutral earth fault. then when she turns on cooker draws current/ imbalance kicks out rcd. She thinks its the sockets that are gone cos Micowave clock goes off etc etc..Its a possibility
Macca
Mar 28, 2008
13,621
297
Hi, Just think it's a bit odd that all was working OK for over 3 weeks then the minute she has new flooring in the kitchen this happens after the cooker has been pulled out and put back..?Cheers
Guiness Drink
cooker certainly sounds like a prime suspect?
most probably somewhere around the cooker to wall-plate connection.
maybe wire pulled loose... touching neutral & earth???
does it trip every time. immediately you turn the cooker on?
or is it only occasionally.
If every time it will be much easier to track & fix! ;)
Is the cooker via a switch with integral socket outlet?
if yes does plugging something in the cooker socket trip anything?
Try a ins res test @ 250v up cooker circuit see if any suss low reading is present?
may need to diss cable from back of cooker and do full ins res @500v to check cables not damaged?
thats all i can think of at the moment! :) ;)
Power Ball
Jul 10, 2008
171
Yorkshire
Thank's for all your quick replies at least i will have plenty of scope when i go tomorrow.
Cheers
Chas Guiness Drink
dean mac
Jul 29, 2008
117
england
I would always put cooker on an RCBO but it sounds like floor fitter has done something during installation.Batty
i never do unless the switch has a socket outlet on it.cookers prone to earth leakage
Feb 27, 2008
11,034
To comply with 17th edition unless cooker circuit is fed down an earthed conduit it will need 30mA Rcd protection. As for leakage currents this is why I would put it on a RCBO rather than through an RCD in split load consumer unit.
Batty
maccarooni
Jul 13, 2008
340
C'mon powerball. what was the problem.
We're all waiting to find out....
Macca
Power Ball
Jul 10, 2008
171
Yorkshire
Thanks Guys
When the floor fitter had moved the cooker and shoved it back he had pushed in the metal box cover on the back of the cooker and both the L and N studs were shorting across this plate and tripping RCD.... just as well she had new CU fitted before the floor covering or she might have got a free curly hair do.!!
Thanks Again for all your help
Cheers
Chas
Power Ball
Jul 10, 2008
171
Yorkshire
All it was, was a lump of flimsey tin in the shape of a box that covered the conections on the back of the cooker. Not very good at all.