Job on my own house , need to move supply /meter  from kitchen to enable forming a downstairs toilet .    

DNO guy  called  to locate where to dig for supply cable  ( Doing it myself)   .  He was a bit nonplussed that I wanted to fit a unit in the meter cupboard to connect  10mtrs  SWA sub-main ....not come across it before.      

I know that they don't want any other gear in there but their own but his boss had agreed as long as they can finish at their sealed DP isolator .   Hence I fitted one myself to make sure there will be room  when the jointers come .         There is   just enough room for cut-out & meter . 

Photo0484.jpg

 
best remove that plastic, highly flammable, non AMD3 compliant REC2 so the DNO can fit their own

there probably used to seeing a bit of SWA bunged straight into meter / REC2 with the earth chopped off

 
Well Deke me ole china, you could have saved yourself the aggravation. Apparently the dnos and Niccy/IET have agreed that a switchfuse is not required in the instance of using swa as meter feed as long as you terminate the swa correctly. 

http://www.charlesendirect.com/products/earthings-accessories.aspx

i have been fitting these on a new build site last year. Everyone is happy with it. :C  

 
Thats what they normally fit ......is'nt it ?     They don't bother about metal enclosures   ie:     Cut-outs  & meters  ..all likely to burst into flames  at any minute  . 

I only held that in place to see if there was room  then thought I may as well fit it as its a bit tight under flameproof , Amd3 ,  bulletproof unit  and have their REC2 off them  .

 
Well Deke me ole china, you could have saved yourself the aggravation. Apparently the dnos and Niccy/IET have agreed that a switchfuse is not required in the instance of using swa as meter feed as long as you terminate the swa correctly. 

http://www.charlesendirect.com/products/earthings-accessories.aspx

i have been fitting these on a new build site last year. Everyone is happy with it. :C  
You jumped in there Sharpie .     That  device is  interesting!!     To my way of thinking , my switch would do but the guy said they have to finish  with  a switch  sealed  on their side .     Which DNO do you deal with ?  

 
I'm guessing the CG box is a switch fuse - so why did you bother with the isolator?

Well Deke me ole china, you could have saved yourself the aggravation. Apparently the dnos and Niccy/IET have agreed that a switchfuse is not required in the instance of using swa as meter feed as long as you terminate the swa correctly. 

http://www.charlesendirect.com/products/earthings-accessories.aspx

i have been fitting these on a new build site last year. Everyone is happy with it. :C  




That's VERY interesting - where is this stated as facts?

 
Give them a call, they will confirm. I believe   I called IET tech line to confirm. 

I think it was either western power or yedl. 

 
Last edited by a moderator:
Give them a call, they will confirm. I believe   I called IET tech line to confirm. 

I think it was either western power or yedl. 


So that's not a blanket approval and unless its in black and white we may as well forget it. The EDF chaps around me, who are ex SEEBoard, are right little hittlers......

 
Well Deke me ole china, you could have saved yourself the aggravation. Apparently the dnos and Niccy/IET have agreed that a switchfuse is not required in the instance of using swa as meter feed as long as you terminate the swa correctly. 

http://www.charlesendirect.com/products/earthings-accessories.aspx

i have been fitting these on a new build site last year. Everyone is happy with it. :C  


i cant see how that would be compliant. you would have single insulated conductors from the SWA

 
So that's not a blanket approval and unless its in black and white we may as well forget it. The EDF chaps around me, who are ex SEEBoard, are right little hittlers......


I was told it is agreed with all dno’s. 

i cant see how that would be compliant. you would have single insulated conductors from the SWA
That was the very reason I checked this out. 

 
Yeah this is Western Power , I think they'll be OK with it .  

As I said  ,  they HAVE to finish at a sealed isolator ...mine  has no sealing facility  , I just needed somewhere to make off the SWA . 




Mind you, given what Sharpend is suggesting we would still need to fit an isolator, then a metal enclosure to make off the SWA!

I still don't see why they need to seal the isolator - as the DNO fuse should have a seal on it, what would sealing the isolator achieve?

 
I still don't see why they need to seal the isolator - as the DNO fuse should have a seal on it, what would sealing the isolator achieve?
I had that on the last new build  ..... long run of meter tails in a bungalow , fitted a KMF  80  with tails awaiting the meter monkey .   He fitted them  but was sent back to squeeze in a DP switch  with seals.      He also left me with this piece of expert nonsense . 

Image004.jpg

 
@Murdoch I quite agree, but then I dont make the rules. 

I had that on the last new build  ..... long run of meter tails in a bungalow , fitted a KMF  80  with tails awaiting the meter monkey .   He fitted them  but was sent back to squeeze in a DP switch  with seals.      He also left me with this piece of expert nonsense . 

View attachment 9138
That must have been his first insulation resistance test! 

 