Hope you enjoyed yourself with a few bevvies on Friday night!Bizarre RCD tripping fault? Probably NOT... {reality generally tends to prove Bizarre is very very rare}
Dubious investigation and testing methods? Possibly YES!
You say you are a 2nd Yr apprentice...
So at this stage it is quite possible you could get distracted up various garden paths by making wrong assumptions...
I would get your head back into the Basics of proving any circuit... ( Be it new install, Alteration, or Faulty existing circuit.. )
You need to confirm if you have dodgy wiring or a failed/failing accessory...
So the first question ALWAYS has to be..
Are there any Electrical Certificates or Periodic Inspection Reports available for the installation and/or the suspect circuit?
Bearing in mind that Electrical certification has been a requirement of BS7671 for a very very long time...
And Part-P related work has required proper certification for 16+ years as that came into effect in April 2006!
If not then keep in mind that not all previous work may have been tested or certified to BS7671
And.. do NOT forget the 'ESSENTIAL GOLDEN RULE OF FAULT FINDING'...
i.e.
Assume EVERYTHING is faulty, Until YOU have proven otherwise...
(Plus do NOT trust anyone else's suggestions, OR any circuit labels or descriptions).
So with the above in mind.. I would probably start with..
[1] disconnect loads and test the RCD to verify that it is working correctly i.e. Not tripping below 15ma..
(A ramp test would be useful if you have access to a suitable tester?)
[2] Do full dead tests of continuity and Insulation Resistance on ALL circuits that you suspect may be relevant to your problem...
[3] Remember to keep the CPC connected to the main earth terminal and any relevant bonding in place, whilst doing IR test, or you could be disconnecting a potential fault path for your IR tests..
[4] Have you checked if the RCD is actually disconnecting BOTH poles? e.g. loft light getting neutral via RCD.. BUT RCD not actually disconnecting the neutral when it trips?
[5] .. Sorry... Friday Night Beer Overload...
Start with points {1] to {4]...
Then come back to us when I am more soberificated!!
Sounds like an interesting case to crack PheonixFoX12!!
Keep going and please keep us updated with your findings.....
Now I shall open another or maybe.. etc..
Whereabouts in Lancashire are you if you are not too far from me maybe I could help you outThanks alot guys for all the inputs into this scenario. Trying my best not to overthink things and keep things simple might not need to jump to testing straight away.
I don't currently have the means of testing the installation but I would say that full dead testing may bring something up. CRIPPER.
What's the likelihood of a borrowed neutral? This problem has not always existed only really in the last few years.
Not taking any offence to these posts im very appreciative of the help
Whats the possibility of that? Could a RCD ramp test prove this?It could of course just be a faulty RCD that is just on the edge of its spec!
Thanks alot for the offer mate much appreciated. However not so sure its that urgent of a problem to be solved as we hardly go up into the loft anyway just for storage really.Whereabouts in Lancashire are you if you are not too far from me maybe I could help you out
As you are an apprentice I was thinking it would be more of a learning opportunity for yourself, I could bring the test gear and my experience and you would get some hands on fault finding experience and guidance as I wasn't planning on doing it all for youThanks alot for the offer mate much appreciated. However not so sure its that urgent of a problem to be solved as we hardly go up into the loft anyway just for storage really.
Just inconvenience for lighting i suppose.