Evening all I would appreciate some input on the following situation..
customer is having a new kitchen fitted.. all cables have been exposed and all ran in unsafe zones some ridiculous wiring of which i have been sorting out.
Joint box above the ceiling with a 2.5 t&e into it and a flex from the jb into the boiler..the t&e ran across a wall into a wall and into the ceiling so I disconnected it and re routed it before reconnecting..
customer is now saying that the boiler isnt responding to the controller..the boiler runs when the programmer is off..the boiler turns off so it is responding to some control maybe a room stat however it then fires up again..
the customer has a Potterton EP2001 Controller with a Feed in and a flex out to a wiring centre with brown being switch live for Hot Water and Green/Yellow (no sleeving) used as switch live for CH
Then in the cupboard upstairs is a 2 port valve a pump and a cylinder stat and a room t'stat on the landing..
Before I get more involved can any experts advise on dealing with any similar issues and pointing me in the direction of the fault ??
Customer says his rads dont warm up.. If the valve is stuck in the hot water position then wouldnt that explain the rads not heating ? But the cable to the boiler has 240 v between L-N on it even when the boiler isnt burning..
your thoughts would be appreciated
customer is having a new kitchen fitted.. all cables have been exposed and all ran in unsafe zones some ridiculous wiring of which i have been sorting out.
Joint box above the ceiling with a 2.5 t&e into it and a flex from the jb into the boiler..the t&e ran across a wall into a wall and into the ceiling so I disconnected it and re routed it before reconnecting..
customer is now saying that the boiler isnt responding to the controller..the boiler runs when the programmer is off..the boiler turns off so it is responding to some control maybe a room stat however it then fires up again..
the customer has a Potterton EP2001 Controller with a Feed in and a flex out to a wiring centre with brown being switch live for Hot Water and Green/Yellow (no sleeving) used as switch live for CH
Then in the cupboard upstairs is a 2 port valve a pump and a cylinder stat and a room t'stat on the landing..
Before I get more involved can any experts advise on dealing with any similar issues and pointing me in the direction of the fault ??
Customer says his rads dont warm up.. If the valve is stuck in the hot water position then wouldnt that explain the rads not heating ? But the cable to the boiler has 240 v between L-N on it even when the boiler isnt burning..
your thoughts would be appreciated