Hi
I'm going to look at connecting up a summer house tomorrow which the customer says he has run a 10mm 3 core armoured to underground (length of run is 25m). In the summer house there is going to be a 20a radial feeding 2 x double sockets and 3 x single sockets, a 6A circuit feeding 23 x Downlights with 5w led lamps and a supply to a hot tub which I am presuming requires a 32A supply but won't know until tomorrow.
If this is the case, am I correct in thinking that 10mm 3 core armoured is big enough?
Sockets = 20A (rated current of circuit breaker)
Lights = 23 x 100w (2300w) or in reality 23 x 5w (115w)
Hot Tub = 32A (assumed circuit size)
Total load = 62A / 52.5A
Supply is PME so will be TT at summer house.
Thanks.
I'm going to look at connecting up a summer house tomorrow which the customer says he has run a 10mm 3 core armoured to underground (length of run is 25m). In the summer house there is going to be a 20a radial feeding 2 x double sockets and 3 x single sockets, a 6A circuit feeding 23 x Downlights with 5w led lamps and a supply to a hot tub which I am presuming requires a 32A supply but won't know until tomorrow.