E Elekk Senior Member Joined May 26, 2010 Messages 108 Reaction score 0 Dec 28, 2010 #1 Can I bunch together several cables in the same tray instead of spacing them apart one cable diameter? Can cables be layered one on top of the other? If yes, how many vertical layers can be placed in the same tray?
danny7299 Well-known member Joined Apr 6, 2008 Messages 880 Reaction score 0 Location Leicestershire Dec 28, 2010 #2 Ate the cables the same voltage , I.e 230/400v or 12/24v ?
E Elekk Senior Member Joined May 26, 2010 Messages 108 Reaction score 0 Dec 28, 2010 #3 The supply voltage for all cables will be 400V three phase and the rating of all cables will be 600/1000V.
Sidewinder The Snake™ Supporting Member Joined May 6, 2010 Messages 15,375 Reaction score 401 Location UK Dec 28, 2010 #4 Yes you can but you need to re-calculate the "loading factors etc." for the modification really to be 100% compliant.
spinlondon Distinguished Member Joined Apr 18, 2009 Messages 1,388 Reaction score 0 Dec 28, 2010 #5 Yes you can, but you will have to de-rate the cables appropriately. The highest I've ever stacked cables is 3 high.
E Elekk Senior Member Joined May 26, 2010 Messages 108 Reaction score 0 Dec 28, 2010 #6 what regulation of BS7671 gives the derating factor for bunched cables (2 high, 3 high, etc)?
Sidewinder The Snake™ Supporting Member Joined May 6, 2010 Messages 15,375 Reaction score 401 Location UK Dec 28, 2010 #7 Spin seems to have his book to hand. I'm sure he will come up with this soon. You will have to calculate for the existing and the new cables. However, are the motors on inverters? Thinking about your other thread.
spinlondon Distinguished Member Joined Apr 18, 2009 Messages 1,388 Reaction score 0 Dec 28, 2010 #8 It's not so mch a Regulation as an Appendix. Appendix 4.
E Elekk Senior Member Joined May 26, 2010 Messages 108 Reaction score 0 Dec 28, 2010 #9 Sidewinder, yes the motors are on inverters...