I'm looking at fitting a new Consumer Unit and the earthing arrangements seems to be TN-C-S (PME) but there is also a Earth Rod connected to the MET.
The house is fed by overhead wire. It turns out that it was converted from TT to TN-C-S but the earth rod connection has been retained. I know I'll need to use the distributor's earth to get a Ze value, but should the earth rod be disconnected or could it be retained going forward?
Is there a case for saying it should be retained as if there was an overhead line fault that only affected the CPC, the house would still have protection via the earth rod?