cheap CU wasn't too bad

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
so i can give a EIC with limited test results?i.e from the CU i can check IR,ring continuity

note on the EIC restricted access jobs a good un?
No, if you test Ir and ring continuity that would be testing stuff outside of the CU.

Test the CU, you could fill at least 2 or 3 pages of a PIR without even having a circuit connected to it.

 
No, if you test Ir and ring continuity that would be testing stuff outside of the CU.Test the CU, you could fill at least 2 or 3 pages of a PIR without even having a circuit connected to it.
but it needs a EIC lurch which is the strange thing as back to the sticker (if fitted) indicates a PIR has been done when it hasn't. only a EIC has been

forum discuss :coat

 
but it needs a EIC lurch which is the strange thing as back to the sticker (if fitted) indicates a PIR has been done when it hasn't because a EIC has beenforum discuss :coat
no. the sticker indicates an inspection has been done, and that it should be periodically tested. unless your stickers have different wording to that in 514.12.1

 
but it needs a EIC lurch which is the strange thing as back to the sticker indicates a PIR has been done when it hasn't because a EIC has been
EIC\PIR. Whatever it needs. General gist is test the CU. Imagine it has no MCB's fitted. Test everything up to that point and note it down. Do a few Zs readings just for peace of mind.

This is why I always say you get a PIR with a CU swap regardless, saves the hassle.

[quote name='Andy

 
but surely the sticker is stating the whole installation has been tested and not just the dbis how id read it?
You can;t tell what has been tested and not tested by looking at the sticker.

The sticker says a test has been done, not what test, or what wasn;t done, or even if it passed or failed, just that some testing was done to something.

 
it doesnt say anything about how much has been tested, it simply says the installation should be periodically I&T ... and the dates of last inspection & next inspection

 
You can;t tell what has been tested and not tested by looking at the sticker. The sticker says a test has been done, not what test, or what wasn;t done, or even if it passed or failed, just that some testing was done to something.
thats miss leading unless change of domestic occupancy requires another pir which i don't think it does?

hmmm ponders

 
thats miss leading unless change of domestic occupancy requires another pir which i don't think it does?hmmm ponders
How is it misleading? I have never understood it as anything different to what I said above, and the wording says what it means, installation tested.

 
How is it misleading? I have never understood it as anything different to what I said above, and the wording says what it means, installation tested.
it really should say part tested if so.

but as andy has said refer to the eic/pir all will be apparent.

but all i'm saying is if sticker says I&T'd no suspicion will make said mortals even think to look at them.

 
you can complete a PIR by simply checking Ze and having a quick look round if you wanted. and still put the same sticker on. you would need to check cert for more info

 
Looks good to me with my limited knowledge just a little question, was told by tutor to run MCBs largest to small largest being nearest to the incoming , is that a regulation or just a best practice issue ?

 
Looks good to me with my limited knowledge just a little question, was told by tutor to run MCBs largest to small largest being nearest to the incoming , is that a regulation or just a best practice issue ?
Best practice issue. Makes no difference in practice though as the busbar is rated for the full load. Wouldn;t make much difference having the usual average household circuits in any order, but if you had a few heavy loads then you'd try to put them as near to the main switch\RCD as possible.

 
Best practice issue. Makes no difference in practice though as the busbar is rated for the full load. Wouldn;t make much difference having the usual average household circuits in any order, but if you had a few heavy loads then you'd try to put them as near to the main switch\RCD as possible.
Thanks buddy :)

 
on the contrary. could even be job example for scheme provider inspection.would it pass?
None complaint with reg 514.12.1

'EVERY' installation shall have a sticker DURABLE enough to last through the life of the installation!

I have been told on numerous occasions that labels & stickers is the most common area of non compliance.

 