Well the Oven and Immersion, both being over 2KW should each be on their own circuit, and neither should be "on the ring" If I could be bothered to open my new yellow book there would be a reg number to quote.
Bathroom light, it is either in or out of the zones. Measure again to be sure which?
0.42 megohm shows there is an issue but no immediate "fault" so further investigation (which usually means the customer waits until the rcd trips)
For something like unearthed fittings, well if the CPC is there and tests okay I connect it there and then rather than even write it down.
Bathroom light, it is either in or out of the zones. Measure again to be sure which?
0.42 megohm shows there is an issue but no immediate "fault" so further investigation (which usually means the customer waits until the rcd trips)
For something like unearthed fittings, well if the CPC is there and tests okay I connect it there and then rather than even write it down.