ok found it.
Requirements of BS7671 connecting the PV a.c. mains.
At the connection to the a.c. mains, the PV supply cable must be connected to the supply side (i.e. upstream) of the OCPD's gor the final circuits in the electrical installation (regulation 712.411.3.2.11).
therefore, the PV supply cable must be a dedicated circuit. It cannot be connected to an existing final circuit of the electrical installation.
When connected in this way, the operation of the protective devices of the other final circuits of the electrical installation is unaffected by the PV installation.
Fault protection
The PV supply cable on the a.c. side must be protected against fault current by an OCPD installed at the connection to the a.c. mains (regulation 712.434.1). A circuit breaker in a one way consumer unit fulfils this requirement.
When an RCD is not required at the PV end
If the purpose of the RCD at the PV inverter end is solely to prove protection against impact, the RCD would not be required if the supply cable was run in a floor or ceiling void, or on the surface or in SWA cable.
Regardless of whether or not the PV inverter has simple separation incorporated, an RCD would not be required in such circumstances.
Shared RCDs are not permitted
At the a.c. mains end the PV supply cable must not be connected to the outgoing way of a final circuit which shares an RCD with other final circuits (see IET code of practise for grid connected PV systems page 88). The reason this is prohibited is that the other final circuits maybe supplied by the inverter, during the shutting down period. This would mean the required maximum disconnection times for these final circuits could be compromised. In addition, sharing an RCD may cause unwanted nuisance tripping due to accumulation of earth currents.
Good afternoon all,
New User here (although I have been an avid reader/spectator a number of years and found the forum a very good source of guidance and advice).
So firstly apologies if reviving this old thread was not the thing to do, but the quote above refers to a number of queries I had around my own PV installation so I thought it the most concise means of asking...
I have an SMA Sunnyboy Inverter installed 2012 into an independent circuit of a Dual RCD consumer unit, and whilst we'd always had infrequent nuisance tripping of the 80A RCD protecting that side of the board, the frequency had increased to the point where it became an inconvenience. (I am aware that PV sharing RCDs is not a good practice from reading these forums, but can only presume that wasn't wide knowledge in 2012 as my New Build home subsequently passed Part P sign-off from my Local Authority).
I had an electrician colleague recently carry out some earth leakage tests on the other circuits which share that RCD in case a cumulative effect was causing it. He found no smoking gun, although he said the results were "not great, but okay".
I carried out a series of investigations where I isolated the PV circuit for weeks at a time and experienced no nuisance tripping whatsoever; with it re-energised I'd typically get a couple a week (between 1-5 times, quite variable in frequency and not definitively linked to weather conditions which I also logged).
I recently requested my MCS installer return to my home to investigate as part of the Inverter 10yr warranty and their electricians stated during their visit that they have see a very small proportion of their installs suffer such nuisance tripping, and cited a recommendation that the PV needn't be RCD protected (I'd also expressed my concern after informing myself on this forum of the effect of a secondary supply sharing an RCD with other sockets).
Their course of action was to relocate the circuit to a non-RCD protected side of the board, which whilst having completely eliminated the nuisance tripping problem, has left me with a few queries.
1. I'd asked them to provide documentation of this modification for my own records, insurance purposes, etc. They seemed surprised that I'd requested this and stated that they could provide a Minor Works Certificate for me - is this the appropriate documentation for this work?
2. I have been reading the available extracts of BS7671, in particular
"522.6.202 Cables in wall less the 50mm from the surface" which I realise stipulates that I require 30mA protection for this circuit - my solar PV cables are within safe zones in plastic capping under render. Now that this circuit has been modified am I required to comply with this (presumably more recent) regulation? I say 'presumably more recent reg' as I believe this was a 2015 update, which our home pre-dates (built 2012).
3. Assuming so, is my only option an independent 30mA RCBO for the the single PV circuit, and hope that without any cumulative leakage effects from the "okay, not great" circuits that this will survive my Sunnyboy inverter switching?
4. I have read a lot of manufacturer advice relating to PV nuisance tripping RCD which focuses on uprating to 100mA or 300mA ratings! Am I right to presume that these are applicable only in cases where cables are routed differently to mine, effectively snookering me (as ours were installed in build, not retro-fitted)?
5. Assuming I do need a 30mA RCBO and this suffers similar nuisance tripping, are my only other options to redesign the wiring routes to not require the RCD protection (Regulation 522.6.204 I think stipulates such examples?), or to upgrade our Inverter which is presumably deteriorating somewhat due to the increased frequency of RCD tripping and its 8 year age (I think we were suggested these had a potential life of 10yrs when we purchased the system, although I got the impression the industry was so new that nobody actually knew this as the time we were quoted it).
Appreciate a number of queries here, but I would really appreciate the guidance / understanding / experiences of anyone whose come across / overcome similar issues so that I can go back to my MCS Installer with an informed response!
Thanks in advance for any support offered.
Cheers