But how would you know that on a cu change if they are plastered in the wall?Although you are only changing the CU, you should still ensure there are no major deviations and the rest of the install is "ok".I class cables out of safe zones as a major deviation and certainly would not just leave it and note it on a cert, which, as we all know, will never see the new owner if the house is sold in the future.
Sorry missed that bit teach me for skipping through but only way these days with some other long threads.Because he has been made aware of it or seen it and is noting it on the cert.Plus the fact this is the reason P was pushed through.
yes. can only be outside a safe zone if mechanically protectedIf its rcd protected does it need to be in the safe zone ?
agreed,An accessory, whether wired in or not, creates a safe zone. A blank plate could create a safe zone if required.
Well I know I have, and I'm pretty certain you have.Im starting to wonder if we have a problem now Lurchio.................................
Aggiue says you are correct,Well I know I have, and I'm pretty certain you have.
Which, in effect, means that you should be doing quite a bit of 'Inspection and Test' of the installation before even starting a CU swap - otherwise, how will you know if any of these conditions exist?There is no legal requirement to bring the existing installation up to the current standards but building regs schedule 1 require it to be no worse in terms of compliance.In terms of the regs we need comply with 131.8, 610.4 and 633.
The electrical safety council give guidance on this and basically states that a consumer unit should not be connected where code 1 conditions apply, though where code 2 or above conditions apply these need to be noted and recommendations made. So in effect you need to make a risk assessment and decide as to whether its safe to install the consumer unit or to connect the circuits to it.