Hi all,

I am currently wiring a new build electrical dwelling consisting of standard domestic circuits ie......up/down ring mains up/down lighting etc.... the issue is the architect is adamant the consumer unit has to be in the store cupboard which is approx 12 metres away from the external metering box outside! Which there fore creates a new sub-main so to be compliant with bs7671 does this need to be rcd protected.....does this need to be time delayed type.

Its just a grey area i have never dealt with before and i am going to speak to napits tech support line tomorrow, but i was just wondering if any of you guys have dealt with this before?

Cheers

James

 
submain is treated the same as normal circuit for if it needs RCD of not. if its TT, it needs an RCD in all cases, in TN, then it may not (i.e SWA, trunking etc)

 
It will need Switch fuse or MCB prtection for overload / fault protection but as has been said IF SWA or in Earthed Metal Trunking then NO RCD required if TN supply.

Last one I did I fitted 100 A Switch fuse back to back with Meter box and wired from their in 3 Core 25mm SWA, which provided more then required CPC to Consumer Unit position.

 
If it's a new build, why couldn't they have put the meter nearer to the CU??

 
It will need Switch fuse or MCB prtection for overload / fault protection but as has been said IF SWA or in Earthed Metal Trunking then NO RCD required if TN supply.Last one I did I fitted 100 A Switch fuse back to back with Meter box and wired from their in 3 Core 25mm SWA, which provided more then required CPC to Consumer Unit position.
tim are you saying if its tn and 3m+ pvc/pvc it needs rcd? why.

and why a switch fuse / mcb?

 
Yes. If the CU is >3M from HED; some form of isolation (switchfuse, 2 pole iso., KMF etc) is needed at the supply end.

IF it is TT, it MUST have RCD protection, regardless of method of install.

If its TN, then as long as you cover the <50mm in walls / earthed sheath / mechanical protection rules, you don`t need the RCD (hence the use of SWA. Most customers deem to prefer it to galv trunking along the hallway:C)

KME

 
tim are you saying if its tn and 3m+ pvc/pvc it needs rcd? why.and why a switch fuse / mcb?
I think KME has already clarified, but NO RCD required for TNS or TNCS.

It may be required for TT to provide Shock protection as earth loop impedence will likely be more then max Zs for the Distribution cct.

Why Switch FUSE?

The DNO will only allow THEIR Service fuse to be used to protect YOUR Meter tails up to 3 Meters in length. More then that then YOU have to provide Fault and overload protection.

 