Hi everyone,
This is my first post so here goes:8}
I first fixed a house back in jan this year at the time the cooker circuit was agreed with customer and a 32a 6.0mm circuit was wired in. Got the call today to go connect cooker up I turn up and a nice shiney range cooker is sat there..............RATED 16 kW!! :_|
Ive sorted a new route for a bigger cable so no problem there but what about isolation standard cooker switches rated 45a. Any suggestions. Thanks in advance. J.