I did the inspection yesterday prior to a CU change (and some other minor works)
The only thing "wrong" is the kitchen which is a later addition single storey extension leaves the CU as a 6mm t&e but in the kitchen it's wired as a ring in 2.5 t&e
I've checked every socket in the kitchen by measurement at each socket to confirm it really is a ring in the kitchen not a 2.5 radial.
So it looks like someone has taken a 6mm from the CU to a junction box somewhere, from there it runs as a ring around the kitchen.
Is it okay to proceed with the CU change and just note this as a departure. While it's certainly unconventional, apart from not yet identifying and checking the junction box, I can't actually see anything unsafe about this.
The only thing "wrong" is the kitchen which is a later addition single storey extension leaves the CU as a 6mm t&e but in the kitchen it's wired as a ring in 2.5 t&e
I've checked every socket in the kitchen by measurement at each socket to confirm it really is a ring in the kitchen not a 2.5 radial.
So it looks like someone has taken a 6mm from the CU to a junction box somewhere, from there it runs as a ring around the kitchen.
Is it okay to proceed with the CU change and just note this as a departure. While it's certainly unconventional, apart from not yet identifying and checking the junction box, I can't actually see anything unsafe about this.