Init:
The regs (and I`m paraphrasing here) ALLOW circuits other than those demonstrated; IF they comply with 7671 OR equivalent.
Ergo; I don`t need to have a diagram of a particular circuit in order to use it.
For instance - I had 2 smoke alarms to wire in a 1 bed flat (D/LD3), surface trunking which passes the CU. So, I take 1 run of 3+E between the alarms; via the CU.
Break all conductors apart from the interlink, and connect `em to the OCPD.
It isn`t shown in 7671 (the source is in the middle of the cct, if you`re being pedantic), but there is nothing wrong with that arrangement, as seen from either 7671 OR 5839-6
In the scenario from the O/P, we have a 6mm radial, on a 30A 3036 - which complies in the basic sense.
we ALSO have a 2.5 ring final, which is effectively fed from the same OCPD - which also complies.
So the only possible issue is the joint.
Or, to look at it another way.
I started a PEL PIR (public entertainment licence periodic) today, in a fair sized hotel.
In the function rooms, they must have, by law, sound level monitoring systems; and an interlink to the fire alarms, which isolates the socket outlets in the event of excessive sound levels, or a fire alarm.
This is done with a remote contactor. The feed to the contactor is a 6mm SWA; the ring then begins at the contactor.
I won`t code that, as I see nothing wrong with it; and its essentially the same circuit we`re arguing over - but there is a contactor at the joint.
KME