And what would you note, as you still haven;t said why it doesn;t comply yet.But, it still does not conform to regs therefore should be noted on the cert as such, which has already been stated.
And what would you note, as you still haven;t said why it doesn;t comply yet.But, it still does not conform to regs therefore should be noted on the cert as such, which has already been stated.
Sadly I don't have a copy of the BRB.You are correct i didnt say why, although i did give a page number of the regs.Page 362
That's an informative appendix, that shows variations on a standard RFC.You are correct i didnt say why, although i did give a page number of the regs.Page 362
I believe this question has been answered. To recap: yes and yes.Is it okay to proceed with the CU change and just note this as a departure?
I see no issues with the testing of this type of circuit.It would not be easy testing it though unless you could get to the join so it is not an ideal situation
Just because a circuit differs from a standard circuit arrangement this does not mean bad practice has been carried out.And i get infractions for suggesting bad practice
No the 6mm wont be a distribution circuit, its a final circuit.hi,wouldnt the 6mm be technicaly a distribution circuit and the the ring the final circuit? if so would the OP's set up contavenne reg 314.4?
"where an installation comprises more than one final circuit each circuit shall be connected to a seperate way in a distribution board. The wiring of each final circuit shall be electrically seperate from that of every ther final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated"
So a 6A lighting RFC will be ok then?Just because a circuit differs from a standard circuit arrangement this does not mean bad practice has been carried out.
nothing wrong with a ring for lighting... not conventional, but nothing dangerousSo a 6A lighting RFC will be ok then?
The same as you would normallyBack OT, how you would record all your dead test results, cable sizes etc???
Spot on:SaluteCan we just point out, for thebenefit of those on whom this hasn`t dawned yet:You can test the ring at ANY point - take a DSO off the wall, and test the ring at that point.
If the readings are satisfactory, you *could* make a note of the fact that there may be a junction box under the floor, where the ring is connected to a 6mm feed; however it is ALSO possible that the 6mm is connected to the ring in the back of a socket - unlikely, but possible, dependant on the terminals.
did this the other day, cpc twisted together in one sleaving buried deep in the cu behind a load of cable, dissconected it from earth bar and did testing from a socketCan we just point out, for the benefit of those on whom this hasn`t dawned yet:You can test the ring at ANY point - take a DSO off the wall, and test the ring at that point.If the readings are satisfactory, you *could* make a note of the fact that there may be a junction box under the floor, where the ring is connected to a 6mm feed; however it is ALSO possible that the 6mm is connected to the ring in the back of a socket - unlikely, but possible, dependant on the terminals.
Apache - you are right, something HAS been said regarding this, a long time ago. I`ve done it, and have no issues with it. All cables are protected, and the list of standard circuits given in the BRB does not preclude the use of other methods.