Been asked today to quote for provision of a 230V supply for a dental x-ray m/c at local surgery, also, to run in control cable between m/c & timer/controller.
Supply OK, running wiring etc. all OK.
HOWEVER, spec / manuf. Inst. calls for no cpc in the control wiring and all info at this stage points to this being 230V, and it also requires flex rather than T&E.
Not too happy about the flex running through the trunking and loft space from wall to wall, but can't really find a reg. that prohibits it. It just seems wrong. Especially with no cpc if it is 230V. If it is F/P/SELV then I would have no issues. I will check with the UK agents tomorrow, it is a Japanese machine.
Just looking for other opinions on the cpc issue and running flex in the fixed install.
As I say it just does not sit right with me and it looks like the equipment connections may not take T&E from the info I have, again I
Supply OK, running wiring etc. all OK.
HOWEVER, spec / manuf. Inst. calls for no cpc in the control wiring and all info at this stage points to this being 230V, and it also requires flex rather than T&E.
Not too happy about the flex running through the trunking and loft space from wall to wall, but can't really find a reg. that prohibits it. It just seems wrong. Especially with no cpc if it is 230V. If it is F/P/SELV then I would have no issues. I will check with the UK agents tomorrow, it is a Japanese machine.
Just looking for other opinions on the cpc issue and running flex in the fixed install.
As I say it just does not sit right with me and it looks like the equipment connections may not take T&E from the info I have, again I