Thanks for your reply.
The sites policy states that caravans have a 16amp supply to each pitch. These caravans are of the static type not tourers.
Sorry should have mentioned that.
It doesn't seem practical to assume all caravans will be pulling 16amps exactly the same time.
Diversity is the question I'm asking. What diversity would one apply to the cable calculation if I was to supply 12 caravans rated at 16 amps each. It wouldn't be practical to do this at full load which would be 192 amps?
If you are hoping for someone to say oh the diversity calculation for static caravans is 75% of the first four vans and 45% of the next eight vans. then you will be disappointed....
You are the one who needs to establish with the customer exactly what they want...
and the types of realistic load expected.
e.g. are the vans only used during holiday periods or are they some of these semi permanent lived in statics? How often is the site full? How many final circuits and what rating are in each van ? etc. etc..
If you go back and re-read about diversity, excluding the few minor common domestic circuits given as illustrations of how diversity can be applied,
it is primarily up to the designer to establish with the client the types of loads and thus supplies needed.
The paragraph in Guidance note 1 Appendix H.. (or appendix A in On-Site-Guide), states that it is impossible to provide standard set of calculations for every installation..
It is your specialist knowledge of the customer and type of installation that they want, that governs what diversity you will consider appropriate or not to apply.
If the site policy states that every user has access to a 16amp supply then maybe you need big cables.
Unless they have a sub-clause saying during busy periods supply may be limited.
I would guess in the real world not many would be pulling more than 10Amps for any significant duration..
How well are they insulated, do they have electric ovens?
A 750watt convector heater can heat up a small area quite comfortably.
What other cooking appliances are included...
Caravan kettles ovens and microwaves can often be lower power item...
But in statics they may be full blown household appliances...
What about vacuum cleaners..?
Are there other existing vans on the site ?
if Yes... what power do they draw?
Guinness