Yes that was what I was asking. It was more about Health and safety as I thought the recomendations these days was just to test sockets and calc everything else. I am just playing catchup after being out of the business for the last 15 years.Ok Tom, if thats what Buildall means then yes it is ok to calculate Zs from adding your Ze or Zdb to your R1+R2, as you have measured both of these then it is a Measured result that you have and can go into the Measured Zs box on the cert.The Niceic recommend this as the safest way to avoid Zs tests at other then socket outlets.
You still have to measure the Ze or Zdb live at the Consumer Unit but at least this is only one test live.
would that depend on what your touching, with what body part, and what your stood on?Buildall dont take this the wrong way but have you ever had a domestic belt. It only tickles lol Id rather do test live too as tom1 says just be careful
Howtesting should be carried out as you go along not once you have finished the job. i like calcualting Zs most of the time as it is safe, and not all shocks tickle. obviously Zs sockets as this this also confirms polarity.
will only confirm live is in the right place. neutral & earth can be wrongobviously Zs sockets as this this also confirms polarity.
But Zs is the 'impedance' of the loop path with parallel paths, so calculating doesn't workCalculating also gives the resistance of the circuit without the parallel paths.
yes, but what if those parallel paths (gas/water) make it comply, but then get changed to plastic?But Zs is the 'impedance' of the loop path with parallel paths, so calculating doesn't work![]()
Ze + R1R2 is a worst scenario of Zs - in reality, Zs is going to be lower, which is usually a good thing.Measuring R1+R2 with nothing connected up, conductors not terminated in CU etc etc, and then adding this to Ze (sometimes from enquiry), is a poor substitute.
How so? Calculation will give you a higher reading than measured if anything so is arguably a better way of doing it as it's unlikely for other parallel paths to alter this reading by other people doing unrelated work etc... at a later date.Measuring R1+R2 with nothing connected up, conductors not terminated in CU etc etc, and then adding this to Ze (sometimes from enquiry), is a poor substitute.