This may sound like a 'mad' question, but it's something I was thinking about the other day.
Scenario:
Ring Final, 32A MCB, RCD protected.
End to End
L - L.....confirmed
N - N....confirmed
CPC - CPC....no continuity
R1 + R2 reading at each socket outlet.........all within 0.05 ohms of each other.
Zs reading at each socket outlet........all within limit for MCB.
So, does the fact that there is no continuity end to end on the CPC matter?
And please, back up your answer with a 'regulation' or a description of 'why' it matters.