It's certainly done that way in the U.S. The NEC requires an earth electrode connected to the neutral at the service entrance.problem, its TNS , not PME,
What is unsafe about having an extra earth electrode on a TN-S or TN-C-S system?
two massively differently systems, dont you even understand the differences in them, let alone TT.?
How is it any different - electrically speaking - from a house which still has a metallic water supply line running multiple tens of feet below ground, and which is required to be bonded?
dont the regs now specifically state you are not allowed such earthing systems?
I wouldn't call changing from TN to TT an upgrade, but still......
you obviously have no conception about earthing systems
And who would be the last person to touch the system? The DNO, surely?
NO, the installation is nothing to do with DNO, he disconnects at the cut out
Should any DNO guy be casually disconnecting a TN earth just because he happens to see an earth rod connected to the MET?
DNO are NOT obliged to provide you with an earth
harks back to fast track,Steptoe,I'm new to the forum, and have read several posts you have made on the merits of various earthing systems.
I don't want to get into a debate about the merits etc.
However, just a question as to how you feel it is possible for a DNO to unilaterally change a supply system, and also not comply with the ESQCR?
Surely they would be in breach of their statutory duty?
IF the DNO provide the earth via TNS/TNCS then they are then legally obliged under ESQCR to maintain it?
they can withdraw this at any time, and as you are providing your own earth they may do so
Are there that many examples of the failure of DNO TNCS systems that you have experienced.
YES
Please excluding the extremely rural borderline TNCS systems that are around, where probably TT would undoubtedly be better suited.
I had a walk around my little village recently with one of our local DNO guys and we counted about 6 earthing rods apart from the local transformer (HV&LV) and the local underground stake on the other LV supply.
He also put in for another 3 or 4 that day, and this is a hamlet of less than 30 houses on the outskirts of a major city.
BTW my house is irrelevant I'm TT!
Paul
prople need to start understanding the fundamentals of earthing systems and the inherent dangers that can be induced by getting the basics wrong.
posts like these should really be in the students section when such things are basic.