A least they have not used the word "illegal "
W️S
W️S
didn't realize it would be subbed out, and by the looks of it subbed out again as the report is from Propcert.co.uk and the actual inspection was done by a local electrician firm in Bexley.
Dear Sir / Madam,
I was wondering if "xxxxxxxxxxxxxxxx" provide Electrical Installation Condition Reports (EICR)?
If you do, I think I can help you by providing a subcontracting service for EICR. Often, we find that some electrical contractors simply don't have the manpower or the time to do testing themselves, and that's where we come in.
Our directly employed electricians arrive in plain white, unbranded vans and can act as your staff and wear your company uniforms (if you provide them). We can even emboss your company details on to our high quality test labels and final reports - in short, the whole service can be made to look like it has come directly from your company. All you need to do is take your customer's order, then give us a call, earning you a passive income whilst your own team undertake other projects.
We undertake this sort of subcontracting for many electrical and facilities companies throughout the UK. Most importantly, quality and safety are also our top priorities,
blah, blah, blah...
If this is something which you’d be interested in speaking about, feel free to email me back or call me on xxxxxxxxxxx
Many thanks,
it will be interesting to see what bull they return with, although it will give us the opportunity to show these up for what they are.I just sent them a note advising them that i have had the report looked at, sent them the quoted parts and asked them if they still think its correct - will see what the "Sales Advisor" (another red flag) comes back with this time, then will let loose with complaints to BG and associations etc...
So I chased and eventually got an update from them:
The main electrician has looked into this and agrees. He has therefore amended the certificate so that it is satisfactory. Please find attached
So they have reversed the C2 finding, as I thought they would, and re-issued the cert - until I went back quoting the regs they were still trying to push the 985GBP work to "fix" the dangerous situation.
Next steps are to go back to BG and let them know what their sub has been up to.
Thanks for all your inputs - the saga will continue!
Toby.
PS - I also got a quote for a new board from a local electrician and will likely get this done later this year for the tenants.