Problems with EICR's is that if you inspect to the 17th ed AMD 3, then nearly ALL properties could fail an inspection - which is sheer madness.
but you always inspect to current regs
Problems with EICR's is that if you inspect to the 17th ed AMD 3, then nearly ALL properties could fail an inspection - which is sheer madness.
but you always inspect to current regs
There's a redacted copy of the EICR at the link below, apologies it took a while to get it here.
http://imgur.com/a/5Xkc4
Let's pick this to bits a bit more.There's a redacted copy of the EICR at the link below, apologies it took a while to get it here.
http://imgur.com/a/5Xkc4
And aren't those breakers BS 3871? yet the EICR says 60698
Except the 40A shower circuit, 5 seconds.All of those circuits should have a 0.4s disconnection time stated, and inspected to.