I'm after advice from those experienced in outdoor temporary supplies really, but all input is welcome.
Firstly, who knows a good supply for 16A splitters? The 2 or 3 way solid plastic ones are what i'm after.
Secondly, I've been asked to run cables for various uses around a field for an event and am struggling with cable sizes!
Using a voltage drop calculator to a max of 9.2V i've got the following maximum lengths:
At 16A loading
1.5mm cable can run up to 17m
2.5mm cable can run up to 30m
(4mm cable can run up to 47m but I haven't any of this!)
At 13A loading
1.5mm cable can run to 22m
2.5mm cable can run to 37m
Which does make me worry about 25m 13A extension reels that normally have 1.5mm flex! Am I missing something? Or is the <9.2V rule not apply to extension leads sometimes?
The event i'm planning is as follows:
Field has 2 x 13A supplies from nearby farm building which is at least 20m away.
17kVA generator with outlets tbc will be on site.
Field is 100m square.
Marquee (15m x 9m) will be in a corner nearest the farm building and have:
sound system requiring 4.5kW in one location.
lighting comprising 12x 30W lamps at 3m spacings.
600W lighting in one location.
900W heater in one location.
In another part of the field, about 10m from marquee, 500W of lighting is needed.
Finally, a tree in middle of field needs supply for 1kW of lighting.
Giving me a challenge and a headache!
Tips please? Thank you!
I'm after advice from those experienced in outdoor temporary supplies really, but all input is welcome.
Firstly, who knows a good supply for 16A splitters? The 2 or 3 way solid plastic ones are what i'm after.
Secondly, I've been asked to run cables for various uses around a field for an event and am struggling with cable sizes!
Using a voltage drop calculator to a max of 9.2V i've got the following maximum lengths:
At 16A loading
1.5mm cable can run up to 17m
2.5mm cable can run up to 30m
(4mm cable can run up to 47m but I haven't any of this!)
At 13A loading
1.5mm cable can run to 22m
2.5mm cable can run to 37m
Which does make me worry about 25m 13A extension reels that normally have 1.5mm flex! Am I missing something? Or is the <9.2V rule not apply to extension leads sometimes?
The event i'm planning is as follows:
Field has 2 x 13A supplies from nearby farm building which is at least 20m away.
17kVA generator with outlets tbc will be on site.
Field is 100m square.
Marquee (15m x 9m) will be in a corner nearest the farm building and have:
sound system requiring 4.5kW in one location.
lighting comprising 12x 30W lamps at 3m spacings.
600W lighting in one location.
900W heater in one location.
In another part of the field, about 10m from marquee, 500W of lighting is needed.
Finally, a tree in middle of field needs supply for 1kW of lighting.
Giving me a challenge and a headache!
Tips please? Thank you!