Well they just quoted mehow much does your main dealership car garage charge for an hours labour?
Well they just quoted mehow much does your main dealership car garage charge for an hours labour?
They have mis informed you, any installation work requires a full EIC for that work, the installation of a new Consumer Unit is also notifiable under the building regulations Part P. Minor works can have a simple certificate, for instance moving a socket, or repairs etc. This kind of work is not minor though. You must insist that you are provided with the proper paperwork.Hello Sidewinder - I think you might be right. They told me that as there is a gas supply to the property no certificate is necessary.
'They' however 'insist' on having a certificate (although not necessary) which is why I have the 'satisfactory' P.I.R. - to them this exceeds requirements.
I have stated that I think I need a E.I.C. and the Buildings Control informed of the installation but they will not agree this.
Thanks for your view.OK Pic 6 & pic 8 show non compliances end of.Do you require assistance to sort this?
It's not for 'them' to agree or disagree with. It's the Law - from Part P of the Building Regulations, echoing the requirements of BS7671.Hello Sidewinder - I think you might be right. They told me that as there is a gas supply to the property no certificate is necessary.
'They' however 'insist' on having a certificate (although not necessary) which is why I have the 'satisfactory' P.I.R. - to them this exceeds requirements.
I have stated that I think I need a E.I.C. and the Buildings Control informed of the installation but they will not agree this.
Hello Manator, thanks for this advice.They have mis informed you, any installation work requires a full EIC for that work, the installation of a new Consumer Unit is also notifiable under the building regulations Part P. Minor works can have a simple certificate, for instance moving a socket, or repairs etc. This kind of work is not minor though. You must insist that you are provided with the proper paperwork.
Hello Theorysparky,Mr Slimare you the Tenant or the landlord of the property ??????
The only option you have left is to report this to the NICEIC, they will take all the details from you. They will then register it as a complaint against the contractor who carried out the works, he will then be given the opportunity to rectify this work. If he does not do this the NICEIC will appoint another electrician to do the remedial works at no cost to yourself.Hello Manator, thanks for this advice. Sadly I have told them this and added that I felt the work was incomplete without the correct paperwork.
I have spent a lot of time trying to convince them but they do not want to listen and relations are now very bad indeed.
Hello Manator and thanks.I am in Aylesbury at the moment, and I am going into London in the morning near Barnet, after that I am going back home, but I will be back London way Tuesday next week, if you need anyone to give a statement on the condition I could help you out.
i think/would hope it will catch there eye and there'll make an example of it and get it sorted.Hello Manator and thanks.I am not sure how this works but I am hoping that my complaint which I will furnish with:
1. the 'unsatisfactory' and 'satisfactory' P.I.R.s
2. the photos of the CU installation
3. the 'list' of required works resulting from the 'unsatisfactory' P.I.R.
4. the detailed 'report' of the works carried out
5. and identifying the documents I think I should have
will encourage N.I.C.E.I.C. to inform the contractor to put everything right and this in turn will filter back to the 'agents' who will see that they were wrong all along etc.
OR am I being naive?
Hello PC - thanks for your views on the photos.pic 1: are those unsheathed tails? tails and earth are untidy and longer than is really necessary. Also no clipping or cable support.
Do the tails and earth go through holes in the top surface? If so there should be a max gap of 1mm around the cables.
pic 5: oh dear, i see the cables do go through a large hole.
And what's that t&e with tape on it? is the sheath short of the enclosure? PVC tape isn't a very professional repair.
pic 8: still no sign of any clips on that bond cable
pic 9: what's this showing us?
pic 11: ah! it's the incoming supply cable - not much you can do about that except perhaps box it in.
pic 13: still no clips on all that height of cable. Rather poor.
Pity we can't see inside that CU
So are you telling us that he has installed a new CU but has NOT issued an Electrical Installation Certificate? And have you recieved a Part P Compliance Certificate from the NICEIC? Can you answer explicitly please
a PIR is just a report on existing installation, any work carried out would need to be covered with a MWC or EIC, then if its notifiable will also need to be cover with a cert from BC. the PIR doesnt cover the replacement of CU.Hello PC - thanks for your views on the photos.Regarding your questions:
1. I have not received an E.I.C.
2. I have not received a Part P Compliance Certificate.
BUT - I have received an 'unsatisfactory' P.I.R. and subsequent to 'remedial' work a 'satisfactory P.I.R.
Then the work is illegal as it does not comply with th eBuilding Regulations untill all such paperwork is in place (within 28 days of the work being carried out).Hello PC - thanks for your views on the photos.Regarding your questions:
1. I have not received an E.I.C.
2. I have not received a Part P Compliance Certificate.
BUT - I have received an 'unsatisfactory' P.I.R. and subsequent to 'remedial' work a 'satisfactory P.I.R.