Ok anyone got any ideas here. I'm thinking processor blown or software malfunction. Anyone else had any issues.
Just one year old fluke 1654b. Zs and ze readings on a PME system 0.01 to 0.05 with a Ka of anything between 8 and 10Ka even when you toggle the f1 and re test. My meter so never been abused or wrongly placed on any circuits.
My kewtec kt60 and my mates fluke 1652 all coming back with ze / zs 0.15 to 0.17 and Ka between 1.25 and 2.1
So I'm right in thinking my fluke 1654b is the problem here.
Swapped a board on a customers house that's where I realised the issue. Re rested my main ze at my house And Ka pefc psc different area same type of readings. Upto 10 Ka. But kewtech and other fluke readings stable
Anyone had issues with these. It's under warranty and actually due for calibration to. So glad I got spare test meters.
Any input appreciate it. Ta