hi guys im wiering a 10amp 3 phase forklift charger that has a 5 pin 16 amp cform on it. just wanted to be sure as i havent done one before.

im going to use a 20 amp 3 pole (D) mcb wired in 4mm singles in trunking to a 32amp rotory isolator

then in 4mm swa to a 16 amp 5 pin female wall mounted socket

then the charger can just be plugged in

can anyone find a fault in this thanks james

 
i thought id use a 20 amp because some forklift charges have a high initial ampage for or so ive read

 
thank for the idea looks like less work there il see if my local wholesaler stocks them.

if i changed the mcb to 16 amp would it hold on the charger start up thanks james

 
thank for the idea looks like less work there il see if my local wholesaler stocks them.if i changed the mcb to 16 amp would it hold on the charger start up thanks james
probably would be fine. check the charger info for more details

 