hi guys im wiering a 10amp 3 phase forklift charger that has a 5 pin 16 amp cform on it. just wanted to be sure as i havent done one before.
im going to use a 20 amp 3 pole (D) mcb wired in 4mm singles in trunking to a 32amp rotory isolator
then in 4mm swa to a 16 amp 5 pin female wall mounted socket
then the charger can just be plugged in
can anyone find a fault in this thanks james