will the DNO replace a head with a fused neutral free of charge?
what should I advise the client?
what should I advise the client?
BS7671 does not apply here as the service cut out would come under the ESQ regulations as cut out belongs to the DNOAFAIK this is a relatively serious safety issue, such that if the neutral fuse blows it can leave energised cables all around the installtion....e.g. Non compliance with....
132.14.1 page 18.
A single-pole, fuse, switch or circuit breaker shall be inserted in the LINE conductor only.
OR
411.3.2.1 page 46.
Automatic disconnection in the event of a fault will disconnect the supply to the LINE conductor.
I believe they have obligations to ensure their supply complies with regs!